    OK Guys and Gals I have a bit of a mystery on my hands.

    Here is the story, I have a shop where I do some wood working, in the past it had a 100 amp electrical service to it, but the service run down to the shop was to be underground, so I ran conductors for a 200 amp service so if I planned to expand I could.

    Well that time came around last year, I added a main vacuum system, and a pop up cutoff saw, the cutoff saw was 3 phase (all I could get) so I installed a rotatory phase converter, this alone took 80 amps to run the 35 amp 3 phase motor on the pop up saw.

    So I upgrade to a 400 amp service to the house and split the load (with a new electrical panel) with 200 amps going down to the shop and 200 for the house, all this has worked fine for about the last 10 months.

    Now for the mystery problem.

    One day I go to turn on the vacuum system (40 amps) and it did not come on, investigating I found the the 40 amp breaker at the shop panel was popped, I reset it and it was fine, and has been working fine since then, yesterday I was doing some layout drawings for the houseboat radio mast welding, I was listening to the stereo and POP out goes the power.

    Now the main power service goes out around here a lot, so I thought mummm power failure time to eat lunch, I get tot he house and the power is back on, OK good, eat lunch and go back to the shop and the powers out down there, I check all the breakers down there and all are fine, I go back up to the house and check the mains there and WHAT the heck!! the main breaker down to the shop had popped, mummmm now what could pop a 200 amp breaker when nothing heavy was running...????...???

    A big mystery....

    If it does it again I'm calling the Ghost busters.

    Any help on this one would take a load off my mind as if my shop is haunted.
    Last edited by Terryl; 05-03-2016 at 05:28 PM.
    ♫♫♫ I知 a lumberjack and I知 OK ♫♫♫ I drink all night and sleep all day. ♫♫♫



    Coming soon to a crop circle near you.....

    There is a 66 and third % chance that I'm on the right planet...

    "I'm happier then a Jackalope in a balloon factory"

    "First rule of testing satellites"
    "If its working fine now, then don't mess with it"

    "Second rule of testing satellites"
    "If you did mess with it, and now it doesn't work, can you blame someone else?"

    "Third rule of testing satellites"
    "If you did mess with it, and it doesn't work now, and you can't blame someone else"
    "Can you HIDE it"?

  2. The Following 2 Users Say Thank You to Terryl For This Useful Post:


  3. #2
    Join Date
    Oct 2012
    Posts
    18
    Satfix Buxs
    312
    Thanks
    2
    Thanked 9x in 6 Posts

    Default

    Have the power company check your meter, could be cut in the underground wire running to shop.

  4. The Following 3 Users Say Thank You to dl76 For This Useful Post:


  5. #3
    Join Date
    Sep 2012
    Posts
    6,231
    Satfix Buxs
    18,711
    Thanks
    38,147
    Thanked 10,243x in 3,573 Posts
    Items beer
Gift received at 10-10-2012, 05:14 PM from JCO
Message: heres your own stein bud.

    Default

    yep... a damaged/crossed main arcing somewhere between the house & the shop would be my guess... but since you have 400 split at the house I'd check to see that it isnt 400 going to the shop now also

  6. The Following 2 Users Say Thank You to hutch For This Useful Post:


  7. #4
    Join Date
    Oct 2012
    Posts
    3,648
    Satfix Buxs
    6,666
    Thanks
    9,060
    Thanked 15,093x in 3,592 Posts
    Items Vintage truck
Gift received at 01-14-2016, 04:33 AM from Wrench

    Default

    Been doing any gardening with a roto tiller or anything of the like because you shouldn`t be popping that circuit unless you are shorting out somewhere enough to cause an arc that would give you the intermittent power outages....just a tick in the wires would be enough at times even if you broke some conduit underground and you`re getting water in the line somewhere. Sounds a lot like you`re arcing out somewhere......check meter, wiring to panel or get the hydro co. out to test your underground lines for full power first aka easiest accessible....if that fails get a shovel and start digging....

  8. The Following 2 Users Say Thank You to The Cobra For This Useful Post:


  9. #5
    Join Date
    Dec 2015
    Posts
    36
    Satfix Buxs
    243
    Thanks
    90
    Thanked 37x in 12 Posts

    Default

    You could trip the main breaker in the shop. Then put an amp clamp on the feed from the house to the shop. The meter should read zero. Anything other than zero and you have a short to ground....

  10. The Following 4 Users Say Thank You to jtpl For This Useful Post:


  11. #6
    Join Date
    Sep 2012
    Posts
    6,594
    Satfix Buxs
    1,923,738
    Thanks
    38,102
    Thanked 36,831x in 6,153 Posts
    Items HookahA BeerFootballGolfACDCGuitar2street BikeCheckered Flag

    Default

    Would be nice to know your conductor sizes,also was the service wire run in pipe. Have you measured voltages from each leg to neutral also between phases.

  12. The Following 2 Users Say Thank You to steveOtoo For This Useful Post:


  13. #7
    Join Date
    Oct 2009
    Posts
    9,003
    Satfix Buxs
    4,002,465
    Thanks
    3,658
    Thanked 8,666x in 3,246 Posts
    Items PhoneHeartVintage truck
Gift received at 12-23-2012, 09:06 AM from ICEMAN
Message: thank you budTVCoffee makerPinkfloydthe travel gnomeTractor

    Default

    Well lets see the wire is #4.0 aluminum in a 3 inch conduit, it's about a 175 foot run, all voltages at the shop are normal as of today, 124 volts on one side 124.1 volts on the other, as asked I threw the breakers at the shop and the main then measured for a short, all reading at over ten meg-ohms between conductors, I even used a megger to check conductor insulation to ground, everything is in the 200 meg-ohms region....


    So whats up?????


    All normal today, you would think if I started up something big (phase converter at 80 amps) I would have a problem???
    ♫♫♫ I知 a lumberjack and I知 OK ♫♫♫ I drink all night and sleep all day. ♫♫♫



    Coming soon to a crop circle near you.....

    There is a 66 and third % chance that I'm on the right planet...

    "I'm happier then a Jackalope in a balloon factory"

    "First rule of testing satellites"
    "If its working fine now, then don't mess with it"

    "Second rule of testing satellites"
    "If you did mess with it, and now it doesn't work, can you blame someone else?"

    "Third rule of testing satellites"
    "If you did mess with it, and it doesn't work now, and you can't blame someone else"
    "Can you HIDE it"?

  14. The Following 2 Users Say Thank You to Terryl For This Useful Post:


  15. #8
    Join Date
    Oct 2012
    Posts
    3,648
    Satfix Buxs
    6,666
    Thanks
    9,060
    Thanked 15,093x in 3,592 Posts
    Items Vintage truck
Gift received at 01-14-2016, 04:33 AM from Wrench

    Default

    Quote Originally Posted by Terryl View Post
    Well lets see the wire is #4.0 aluminum in a 3 inch conduit, it's about a 175 foot run, all voltages at the shop are normal as of today, 124 volts on one side 124.1 volts on the other, as asked I threw the breakers at the shop and the main then measured for a short, all reading at over ten meg-ohms between conductors, I even used a megger to check conductor insulation to ground, everything is in the 200 meg-ohms region....


    So whats up?????


    All normal today, you would think if I started up something big (phase converter at 80 amps) I would have a problem???
    OOOPS....Terry did I see aluminum wiring???? That sends up a red flag to me. In my experience I`ve had many problems with it in the past to the point of recommending it be stripped in several renos I`ve done. Problem lies with wherever the aluminum and copper join, be it switches, plugs, breakers etc etc......Copper and aluminum heat and cool at different rates and becomes "loose" at the connection causing arcing after using it for a short while. When the wires cool(are off) they will work again until the heat builds expanding the wires at different rates causing the arcing. The cycle will continue indefinitely and drive you nuts. That is a big part of the reason they don`t use aluminum wiring in houses anymore(at least in Ontario). It`s not the wiring but the copper/aluminum joining together that MAY be your problem. I`d bet on it.
    Even (as silly as it sounds) a slightly overturned marrett can squash aluminum wiring enough to the point of fracture causing an arc when heated and when the wire cools it works fine....till it heats up again. I wouldn`t believe it but I`ve seen it happen more than once.
    Last edited by The Cobra; 05-04-2016 at 03:09 AM.

  16. The Following 5 Users Say Thank You to The Cobra For This Useful Post:


  17. #9
    Join Date
    Sep 2012
    Posts
    6,594
    Satfix Buxs
    1,923,738
    Thanks
    38,102
    Thanked 36,831x in 6,153 Posts
    Items HookahA BeerFootballGolfACDCGuitar2street BikeCheckered Flag

    Default

    Looks like no shorting going on between conductors, just wondering what the cross phase voltage is, usually around 247 volts. A possibility might be in how many of your neighbors share the same transformer. I have seen as many as 7 households on one transformer. Sometimes they go bad.

  18. The Following 3 Users Say Thank You to steveOtoo For This Useful Post:


  19. #10
    Join Date
    Oct 2009
    Posts
    9,003
    Satfix Buxs
    4,002,465
    Thanks
    3,658
    Thanked 8,666x in 3,246 Posts
    Items PhoneHeartVintage truck
Gift received at 12-23-2012, 09:06 AM from ICEMAN
Message: thank you budTVCoffee makerPinkfloydthe travel gnomeTractor

    Default

    Well 4.0 aluminum was a ton cheaper then 2.0 copper, at 175 foot plus the connections at the boxes it was way cheaper then copper (at that time) stripping it out is not an option, not when it's buried 4 feet under ground, we had a tractor to help in the pulling.

    One spool and lots of pulling lube.

    And I on a regular bases pull the main connections and no-ox lube them then re-tighten them, I know about the possible problems with aluminum wire.
    ♫♫♫ I知 a lumberjack and I知 OK ♫♫♫ I drink all night and sleep all day. ♫♫♫



    Coming soon to a crop circle near you.....

    There is a 66 and third % chance that I'm on the right planet...

    "I'm happier then a Jackalope in a balloon factory"

    "First rule of testing satellites"
    "If its working fine now, then don't mess with it"

    "Second rule of testing satellites"
    "If you did mess with it, and now it doesn't work, can you blame someone else?"

    "Third rule of testing satellites"
    "If you did mess with it, and it doesn't work now, and you can't blame someone else"
    "Can you HIDE it"?

  20. The Following 2 Users Say Thank You to Terryl For This Useful Post:


  21. #11
    Join Date
    Sep 2012
    Posts
    6,594
    Satfix Buxs
    1,923,738
    Thanks
    38,102
    Thanked 36,831x in 6,153 Posts
    Items HookahA BeerFootballGolfACDCGuitar2street BikeCheckered Flag

    Default

    Quote Originally Posted by The Cobra View Post
    OOOPS....Terry did I see aluminum wiring???? That sends up a red flag to me. In my experience I`ve had many problems with it in the past to the point of recommending it be stripped in several renos I`ve done. Problem lies with wherever the aluminum and copper join, be it switches, plugs, breakers etc etc......Copper and aluminum heat and cool at different rates and becomes "loose" at the connection causing arcing after using it for a short while. When the wires cool(are off) they will work again until the heat builds expanding the wires at different rates causing the arcing. The cycle will continue indefinitely and drive you nuts. That is a big part of the reason they don`t use aluminum wiring in houses anymore(at least in Ontario). It`s not the wiring but the copper/aluminum joining together that MAY be your problem. I`d bet on it.
    Even (as silly as it sounds) a slightly overturned marrett can squash aluminum wiring enough to the point of fracture causing an arc when heated and when the wire cools it works fine....till it heats up again. I wouldn`t believe it but I`ve seen it happen more than once.
    Aluminum service conductors are still accepted almost everywhere. All meter cans are approved with al/cu lugs and the conductors should be coated with an antioxidant. Joining cu with al should be done with a proper split bolt connector. Usually problems with aluminum occur with wire under #6 gauge. The Cobra could have a point, maybe a loose lug or connector.

  22. The Following 2 Users Say Thank You to steveOtoo For This Useful Post:


  23. #12
    Join Date
    Sep 2012
    Posts
    6,594
    Satfix Buxs
    1,923,738
    Thanks
    38,102
    Thanked 36,831x in 6,153 Posts
    Items HookahA BeerFootballGolfACDCGuitar2street BikeCheckered Flag

    Default

    On your cut/off saw is it starting normally or have you noticed a difference. In a rotary phase converter there is usually a bank of 6 or more 40u/f caps in series that make up the artificial leg. I have seen these caps go bad many times

  24. The Following 2 Users Say Thank You to steveOtoo For This Useful Post:


  25. #13
    Join Date
    Sep 2012
    Posts
    6,231
    Satfix Buxs
    18,711
    Thanks
    38,147
    Thanked 10,243x in 3,573 Posts
    Items beer
Gift received at 10-10-2012, 05:14 PM from JCO
Message: heres your own stein bud.

    Default

    I am not a fan of aluminum either... hopefully all splices are above ground & you can find the loose connection quickly

  26. The Following 3 Users Say Thank You to hutch For This Useful Post:


  27. #14
    Join Date
    Oct 2012
    Posts
    3,648
    Satfix Buxs
    6,666
    Thanks
    9,060
    Thanked 15,093x in 3,592 Posts
    Items Vintage truck
Gift received at 01-14-2016, 04:33 AM from Wrench

    Default

    I ran your problem by our site guy this aft....and after his swearing tirade about aluminum wiring he muttered something about you melting down all of it and making beer cans with it.
    OK seriously he also thinks you probably have a short that`s arcing when hot and the wires expand....nothing much to test unless you`re running a test exactly when it happens and then run the test again when it starts working...a lot of time and trouble and could get expensive depending on who is doing the tests etc.
    His suggestion was to manually inspect and test where possible any GFIs, connections, breakers, caps etc etc...he also believes it`s a short from your post but finding it can be a pain.
    Let us know what it ends up being.

  28. The Following 2 Users Say Thank You to The Cobra For This Useful Post:


  29. #15
    Join Date
    Oct 2009
    Posts
    9,003
    Satfix Buxs
    4,002,465
    Thanks
    3,658
    Thanked 8,666x in 3,246 Posts
    Items PhoneHeartVintage truck
Gift received at 12-23-2012, 09:06 AM from ICEMAN
Message: thank you budTVCoffee makerPinkfloydthe travel gnomeTractor

    Default

    Quote Originally Posted by steveOtoo View Post
    On your cut/off saw is it starting normally or have you noticed a difference. In a rotary phase converter there is usually a bank of 6 or more 40u/f caps in series that make up the artificial leg. I have seen these caps go bad many times
    Well everything has been running fine for the last few days, ran all the equipment that takes a big load, and nothing happened, all breakers are normal.

    I cycled the phase converter on and off several times (about 5 min between cycles) with the main dust collector on line for a total load of around 120 amps and all is well...If it happens again I will call in the reinforcements, the electricians that installed the new 400 amp service to take a look.
    ♫♫♫ I知 a lumberjack and I知 OK ♫♫♫ I drink all night and sleep all day. ♫♫♫



    Coming soon to a crop circle near you.....

    There is a 66 and third % chance that I'm on the right planet...

    "I'm happier then a Jackalope in a balloon factory"

    "First rule of testing satellites"
    "If its working fine now, then don't mess with it"

    "Second rule of testing satellites"
    "If you did mess with it, and now it doesn't work, can you blame someone else?"

    "Third rule of testing satellites"
    "If you did mess with it, and it doesn't work now, and you can't blame someone else"
    "Can you HIDE it"?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •